Mesh filters allow more airflow, when clean,and seem to get more grease out of the air stream than the baffle filters. The reason NFPA 96 does not allow the mesh filters is that flame goes right through them, allowing flame to continue up the plenum and duct. The baffle filters make the flame go through 2 direction changes of 180 degrees. I have found more insurance companies requiring baffle filters than any of the fire/building inspectors. I can sometimes sell a baffle filter because the mesh filters get so much grease build-up that they allow almost no air flow.
Remember, the NFPA codes are a model code. They are not law until accepted as such by the law making agency. Then they have to be enforced by someone. When speaking of the NFPA codes, there may be several versions of the same basic code. For instance, we speak of NFPA 96, when we should be more specific and refer to NFPA 96-1994 or NFPA 96-1998 or the current NFPA 96-2001. Most NFPA codes are reviewed every three years, and revised as decided on the the committee. However, the day you go to court, the opposing attorney will probably refer to the current NFPA code whether it has been adopted by your jurisdiction or not. Part of the reasoning is that you as an expert, are held to a higher standard than your customer.
Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc