Re: Crazy Burner Problem
If you decide to create/replace/re-wire the protective control circuit, use a relay that is set up in the Normally Closed position for the operation of the burner/blower. This way if the relay itself should fail (relay coil go bad) it won't shut you down. Use a plug in style relay, so replacements can be quick and painless.
All the safety devices (high temp limit, flow control, high pressure cut off, etc.) should be supplied with a positive wire to one side of their Normally Open contacts, with the other contact connected to one of the relay coil terminals. The other contact on the relay coil control contact should be connected to ground or neutral (if a 110VAC relay is used) the relay's contacts (NC) should control the power feed to the burner/blower so if the safety's activate, the relay engages, and the connection to the burner is broken. any ONE of the safety devices should be able to energize the relay and disconnect the burner. Using this design, saves the relay coil from premature failure due to it being energized whenever the machine is powered up.
This type of an extra safety system can be added to any style hot/steam machine as an added extra layer of protection for your equipment.
Most Radio Shacks or electrical supply stores have the relays, and the PW equipment dealers have the safety devices. (just be sure that the LOAD rating for the relay is rated HIGHER than the amperage of your blower/burner motor)
Just my $0.02 worth
Rich
rmepowerwashing.com