Beckett Cleancut Fuel Pump

Steven Button

Administrator
Can I mount a pressure gauge on a Beckett Cleancut Fuel Pump's bleeder port?

Also, should the fuel pressure be at 140 psi? I am reading that it is set at 100psi at the factory - should I stick with this?
 

Paul Kassander

New member
Usually the burners are set between 120-140 depends on the brand-manufacture and how the air bands are adjusted. I have had to raise and lower the pressure a little in that range to get them to burn clean sometimes. I would have to look again but I think there is a gauge port on the side of the pump.
 

Russ Johnson

Equipment Expert
I believe you have to make an adapter for the copper tubing and test the pressure at the outlet. I personally hate that fuel pump. I've seen the solenoid valve go bad, and fuel keeps dumping, at a much reduced flow, into the combustion chamber. There's no gauge port, and no cutout pressure adjustment. I rarely replace a clean cut, but instead replace it with an A2VA-7116 fuel pump and the solenoid that is required for the machine voltage and a brass outlet fitting.

And...140 or so is where you want to be with #2 oil or diesel. Kerosene doesn't require that much pressure (100 - 120) to properly atomize for a clean burn. Diesel needs the extra pressure to mist out right. Diesel does, however, offer better lubrication to the fuel pump.

you know, ages ago, (and I was there, yes..) burners had to be set for the fuel type. They used different air cones and fuel pressures to properly combust diesel (#2 oil) or kerosene (#1 oil).
 

Steven Button

Administrator
Usually the burners are set between 120-140 depends on the brand-manufacture and how the air bands are adjusted. I have had to raise and lower the pressure a little in that range to get them to burn clean sometimes. I would have to look again but I think there is a gauge port on the side of the pump.

Thanks Paul, went to mount the gauge today and noticed that it is not a Suntec fuel pump... reduced burner nozzle size on Largo hot box from 3.00gph to 2.50 gph and adjusted the air bands for clean burn - wanted to check pressure since I changed these other things and noticed there is no gauge port.

I believe you have to make an adapter for the copper tubing and test the pressure at the outlet. I personally hate that fuel pump. I've seen the solenoid valve go bad, and fuel keeps dumping, at a much reduced flow, into the combustion chamber. There's no gauge port, and no cutout pressure adjustment. I rarely replace a clean cut, but instead replace it with an A2VA-7116 fuel pump and the solenoid that is required for the machine voltage and a brass outlet fitting.

And...140 or so is where you want to be with #2 oil or diesel. Kerosene doesn't require that much pressure (100 - 120) to properly atomize for a clean burn. Diesel needs the extra pressure to mist out right. Diesel does, however, offer better lubrication to the fuel pump.

you know, ages ago, (and I was there, yes..) burners had to be set for the fuel type. They used different air cones and fuel pressures to properly combust diesel (#2 oil) or kerosene (#1 oil).

Russ, the fuel keeps dumping after trigger gun is released?

I was trying to read up on fuel pressures and came across what you are saying about different air cones and such related to different fuel types...

Us young(er) guys have got it a whole lot easier than our predecessors!
 

greg/sd

New member
Steven do you remember when my coil blew up in the parking garage. guess what kind of burner motor was on it. fuel solenoid stuck open and kept dumping fuel in the chamber Kaboom
 

Steven Button

Administrator
So... Do I replace the pump, or can I just replace the solenoid to avoid something like this happening? The coils do have pressure relief valves, thermostats and flow switches, should that not be sufficient to avoid the coil blowing?
 